Good morning all


I have obtained the following [I feel as the] 'best we can do for now' information from the DNO. They were helpful in my test case request for info.


"...address 1:

LV underground - 362m

HV underground to primary-  2000m

No Surge protection devices


address 2:

LV underground to substation - 110 m

HV UG from substation to HV pole is 823m then 301m 11kV overhead then 190m HV UG to the primary substation.

Distance to cable termination with surge protection device from secondary substation is 1124m (823m 11kV UG + 301m 11kV Overhead).  The nearest cable

termination does not have surge protection installed. ..."


In relation to the risk assessment equation variables dealing with distribution cable lengths  ie. the Lpal Lpcl Lpah Lpch, how would one fit the given values into the variables ?


For addr1, ignore the HV (e.g. use zero for Lpah Lpch),  then take Lpcl as 362 and Lpal as 638 ?


For addr2, i'm not sure on this one ?


Thanks for your input.

Habs


Parents
  • I think this is also linked to how standards relate to contracts, specifications and the expectations of clients - and how BS 7671 might be used to get more out of a contractor than they quoted for on occasion?


    So, for example, you could level the same arguments at Section 444 and assume that you've just got to go the whole hog on EMC. However, the industry is very happy working with 444 and assuming that, for the most part, many installations won't require the all-singing, all-dancing approach, including the use of BS EN 50310, and not every installation will comply with every requirement in 444.


    The big difference I guess with 443/534 being that of claims if and when equipment starts "popping".
Reply
  • I think this is also linked to how standards relate to contracts, specifications and the expectations of clients - and how BS 7671 might be used to get more out of a contractor than they quoted for on occasion?


    So, for example, you could level the same arguments at Section 444 and assume that you've just got to go the whole hog on EMC. However, the industry is very happy working with 444 and assuming that, for the most part, many installations won't require the all-singing, all-dancing approach, including the use of BS EN 50310, and not every installation will comply with every requirement in 444.


    The big difference I guess with 443/534 being that of claims if and when equipment starts "popping".