AJJewsbury:
Overhead supply or LPS fitted
I can see the sense of that, but I can only see the LPS bit mentioned in BS 7671 (534.4.1.3) - is the overhead line bit mentioned somewhere else in BS 7671 or is that just accepted good practice that has escaped our regs?
- Andy.
534.4.1.3 (cryptically).
... overhead lines (including LV) are not unknown to suffer direct strike, and therefore "or protection against the effects of direct lightning" may well apply.