Alasdair Anderson:
Better - the optimum path for the lightning strike is now your neighbour's aerial......
A long time since I did this at university (or possibly earlier) but dredging my memory banks, the reason lightning conductors are sharp spikes is that the radius of the tip (i.e. how sharp it is) affects the ionisation potential and so makes it a more attractive conductor for lightning. If there is a roof in the way it should make a big difference, particularly if it is raining and the roof is wet, a high probability in a thunderstorm. Of course if your house is on a hill and you have no neighbours it may still make your house the most likely point to be struck.
psychicwarrior:
Forgive me to come back to this again, but...
Take a *row* of small shops in a town centre all joined together, just for instance. e.g. Urban, commercial and no LPS on the row.
Reading the Regs, it is mentioned that SPDs are for transients from atmospheric and from switching - but it details that concern is for switching from *within* the installation only, as I read it.
Therefore if the example shop is not concerned with internal switching i.e. it only has a till and some lights, then the concern is only with atmospheric.
Given a shop is a commercial activity, a risk assessment approach cannot be taken and Regs state fit a SPD; as an aside, this applies it seems, even if it is a shop selling junk and a shop floor the size of a six-pence and a domestic probably has more 'value' in it. Given there is no LPS on the shop (or the row of), then its a TYPE 2 SPD near the origin (well, in the shop DB). Correct please ?
oh and only when an LPS is fitted is a TYPE 1 required too (or a 1+2). ?
Regards
Habs
gkenyon:
psychicwarrior:
Forgive me to come back to this again, but...
Take a *row* of small shops in a town centre all joined together, just for instance. e.g. Urban, commercial and no LPS on the row.
Reading the Regs, it is mentioned that SPDs are for transients from atmospheric and from switching - but it details that concern is for switching from *within* the installation only, as I read it.
Therefore if the example shop is not concerned with internal switching i.e. it only has a till and some lights, then the concern is only with atmospheric.
Given a shop is a commercial activity, a risk assessment approach cannot be taken and Regs state fit a SPD; as an aside, this applies it seems, even if it is a shop selling junk and a shop floor the size of a six-pence and a domestic probably has more 'value' in it. Given there is no LPS on the shop (or the row of), then its a TYPE 2 SPD near the origin (well, in the shop DB). Correct please ?
oh and only when an LPS is fitted is a TYPE 1 required too (or a 1+2). ?
Regards
HabsAll of these questions are answered in sections 3.7.2 and 3.7.3 of the OSG (pp39-41 of the current edition).
psychicwarrior:
gkenyon:
psychicwarrior:
Forgive me to come back to this again, but...
Take a *row* of small shops in a town centre all joined together, just for instance. e.g. Urban, commercial and no LPS on the row.
Reading the Regs, it is mentioned that SPDs are for transients from atmospheric and from switching - but it details that concern is for switching from *within* the installation only, as I read it.
Therefore if the example shop is not concerned with internal switching i.e. it only has a till and some lights, then the concern is only with atmospheric.
Given a shop is a commercial activity, a risk assessment approach cannot be taken and Regs state fit a SPD; as an aside, this applies it seems, even if it is a shop selling junk and a shop floor the size of a six-pence and a domestic probably has more 'value' in it. Given there is no LPS on the shop (or the row of), then its a TYPE 2 SPD near the origin (well, in the shop DB). Correct please ?
oh and only when an LPS is fitted is a TYPE 1 required too (or a 1+2). ?
Regards
HabsAll of these questions are answered in sections 3.7.2 and 3.7.3 of the OSG (pp39-41 of the current edition).
My good man, with respect I say, as are a lot of questions raised on here covered/answered in the usual and other publications !
I am sorry my question caused that big sigh from you :-) I do read before I ask anything...perhaps that just makes it worse haha
A simple brief yes, no discussion perhaps just to see if I understood what I read.
Take a *row* of small shops in a town centre all joined together, just for instance. e.g. Urban, commercial and no LPS on the row.
Reading the Regs, it is mentioned that SPDs are for transients from atmospheric and from switching - but it details that concern is for switching from *within* the installation only, as I read it.
Therefore if the example shop is not concerned with internal switching i.e. it only has a till and some lights, then the concern is only with atmospheric.
Given a shop is a commercial activity, a risk assessment approach cannot be taken and Regs state fit a SPD; as an aside, this applies it seems, even if it is a shop selling junk and a shop floor the size of a six-pence and a domestic probably has more 'value' in it.
Given there is no LPS on the shop (or the row of), then its a TYPE 2 SPD near the origin (well, in the shop DB). Correct please ?
oh and only when an LPS is fitted is a TYPE 1 required too (or a 1+2). ?
Overhead supply or LPS fitted