The Swiss Way



We recently had our kitchen rebuilt and at the same time the distribution box was updated. Here are a few pictures to show a non UK installation. The supply is 3 phase 20A per phase. Lights and sockets are generally 1.5mm2  singles in conduit. Appliance power (2 or 3 phase) is usually cables in conduit. Sockets and lights are on the same circuit for a large room or a number of small rooms. Neutral used to be yellow and is now blue. Phases are red, white and black. Circuits after the switch can be any other colour.

64fe214e3a32373cfc13fd3fbe5acb1d-huge-01-bare-kitchen.jpg


Bare kitchen with first fix cabling

c8e58ae6697dc5cf980ca9d0337030aa-huge-02-ready-for-a-light-fitting.jpg


Ready for a light fitting

d27806d930806064e9394b54aefd6b84-huge-03-old-distribution-box-with-new-cables.jpg


The bottle fuses were for the appliances, 2 phase for the oven and hob and 3 phase for the dishwasher. The Bathroom and toilet had an RCD. The bedrooms and living room MCBs with neutral isolators.

3d5cf47b80207873e579b996534ead17-huge-04-swiss-plasterers-fill-the-boxes-as-well.jpg


Plasterers are the same everywhere.

82c35cdf1a47626fa161e9e19332df02-huge-06-space-for-the-oven-and-fridge-freezer.jpg


Space for the oven and fridge freezer with wiring.

2de8561beed4864fb2e2b66c36f58a9e-huge-07-wiring-for-the-hob-and-sockets.jpg


Wiring for the hob (cable) and sockets (singles).

1b1ec8c3f2fc3dcbf6d148774ced568d-huge-08-rebuilt-distribution-box.jpg


New distribution box. 3 phase MCBs for the oven and hob. RCDs for the dishwasher and lighting and power circuits.

33f52c124fa13fc9ed9db64aa66f203d-huge-09-documentation.jpg
592124a253ca1c378a7623a6ce6586c3-huge-10-supply-details.jpg


Supply details

8af10914d97f61cc680fa0e3ba8fef3d-huge-11-incoming-cable-to-the-block.jpg


Incoming cable to the block (6 apartments)

055ddf1b1dbbd9ab11b324ba7e0ad679-huge-12-meter-cupboard.jpg


Meter cupboard


.37d54f8a56d370a0ae7c78b8596399c4-huge-13-finished.jpg


Finished ?


Best regards


Roger



  • Andy, it appears that the Swiss definition of TN-S is slightly different and applies after the main fuse. The attached picture is taken from 'Elektrische Installationen und Apparate by H. R. Ris' (just to avoid any copyright problems ? ). What is described as TN-S is after the main fuse. What is described as TN-C keeps the PEN right to the point of use as long as it is larger than 10mm2. TN-S-C combines both, splitting the neutral and earth when the CSA drops below 10mm2.


    Z, A nice tool, but as ever made in Germany and labelled in English ?


    Best regards


    Roger

    cf9a17ff24f36dc99340196b38d85a15-huge-tnsc.jpg
  • Der Schutzleite PE wird ab der Anschlussicherung abgefurt..

    (the protective cable PE is lead off separately from the (place of ) the connexion fuses )

    WOW !

    So much for IEC standardization. 

    To me that, and more important , to  IEC 60364   would be  TNC-s, namely TNC on the big side, and s on the small side.


    Interessant zu lesen aber.


  • It's not just the Swiss that are confused on that point - it's only with the 18th Ed have we got rid of the phrase "The usual form of TN-C-S is as show, where the supply is TN-C and the arrangement in the installation is TN-S."  from fig 3.9 of BS 7671 (my emphasis).


      - Andy.