Hello IET guys 


I have a problem where a cable installed on site doesn't comply to Bs7671 current  carrying capacity for underground cable reference method D 


the engineer who design the cable used amtech and data from bicc with reference method 110. 


Dose bicc comply? As its old data for cables install in any country from what I can see. I would have thought bs7671 design must be used? 

Parents
  • Thanks guys. 


    Im looking at this from a testing point of view so I don’t have all the answers. I’m just trying to understand the numbers 


    1 Depth of lay - 1m


    2 - Spacing - 4” ducked? 


    3 - In ducts or buried direct - duck 


    4 - Ground Temperature - 20C A’s guess 


    5 - Soil Thermal Resistivity. Not too sure. I understand the area has a very high water table 


    6 - air temperature - normal uk of 30C 


    250a 60947-2 prob max load of 220a lugged connection  to 250 60947-3 


    regard 


    tony
Reply
  • Thanks guys. 


    Im looking at this from a testing point of view so I don’t have all the answers. I’m just trying to understand the numbers 


    1 Depth of lay - 1m


    2 - Spacing - 4” ducked? 


    3 - In ducts or buried direct - duck 


    4 - Ground Temperature - 20C A’s guess 


    5 - Soil Thermal Resistivity. Not too sure. I understand the area has a very high water table 


    6 - air temperature - normal uk of 30C 


    250a 60947-2 prob max load of 220a lugged connection  to 250 60947-3 


    regard 


    tony