BICC or BS7671 comply for design

Hello IET guys 


I have a problem where a cable installed on site doesn't comply to Bs7671 current  carrying capacity for underground cable reference method D 


the engineer who design the cable used amtech and data from bicc with reference method 110. 


Dose bicc comply? As its old data for cables install in any country from what I can see. I would have thought bs7671 design must be used? 

Parents
  • Thank you oms


    i completed my 2396 design recently and find myself checking everything. I now have a copy of the bicc and intend on spending time learn more on the cable selection. 


    The reason I was doubting it so much was because the engineer response to my question was “amtech selected the cable”


    thanks again for for your help
Reply
  • Thank you oms


    i completed my 2396 design recently and find myself checking everything. I now have a copy of the bicc and intend on spending time learn more on the cable selection. 


    The reason I was doubting it so much was because the engineer response to my question was “amtech selected the cable”


    thanks again for for your help