Low current Zs test tripping RCBO

Hi


Have a question about RCD testing. I'm not new to testing and have been doing it for quite a few years now but have come across something that has never happened before.


On Zs testing a circuits on a DB with all RCBOs every one of them trip on a 2 wire low test. I didn't find this out until I did the lighting as the sockets use 3 wire and I allow the default selection of 3 wire low. Using Megger MFT. All 3 lighting circuits did this. I used a 3 wire low (using 3 probes) and they didn't trip. I tried the socket circuits on 2 wire low and they did trip.

All load turned off.


I'm guessing the use of the neutral in the test allows some balancing current through the RCBO but then I don't know the technical differences between 2 and 3 wire low test and can't find any details on it anywhere. I suspect, even if I could find it it may go into so much detail it would go over my head.


The question is why are they tripping? No Load. IR tests all >999. 


Anyone got any Ideas?


Parents
  • Hello,  I have also had this issue whilst Zs testing 2 lead low with a megger MFT1730.  Just bought a 1741 for the works kit and I've not used it for Zs testing on two lead yet.  I'm curious now.

    I'm going to throw confusion into the works though, because I was advised to swap the two leads over at the Megger - so plug the green into the red slot and the red into the green slot.  I don't know what the machine does differently down the cores but it works a treat.  Also with the plug tester, plugged in back to front on two leads.

    Zs
Reply
  • Hello,  I have also had this issue whilst Zs testing 2 lead low with a megger MFT1730.  Just bought a 1741 for the works kit and I've not used it for Zs testing on two lead yet.  I'm curious now.

    I'm going to throw confusion into the works though, because I was advised to swap the two leads over at the Megger - so plug the green into the red slot and the red into the green slot.  I don't know what the machine does differently down the cores but it works a treat.  Also with the plug tester, plugged in back to front on two leads.

    Zs