Neutral Voltage Question

Hi all, 


Hoping someone can help with this, as it bothering me that I dont know this. 


This is quite tricky to explain without an image. Essentially, if we have a circuit supplying one luminaire. The line conductor has a voltage of 230v from earth potential supplying the light. To complete the circuit, on the return leg a neutral is required (<50v from earth potential). Where is the point where the neutral is no longer at mains voltage, is it at the neural terminals? 


Is it a case of the luminaire will "use up" the supplied mains voltage? 


Any assistance is appreciated. 


Thanks
Parents

  • It also assumes equal conductor size for Line and Neutral



    Indeed it does - which might not be a safe assumption since some older 3-phase systems employed a half-sized N. So if you happen to be on the end of an old 3-phase cable where only one phase is significantly used and no parallel paths with N you could see two-thirds of the v.d. along N instead of half - so maybe 24.53V might be closer in some cases.


       - Andy.


Reply

  • It also assumes equal conductor size for Line and Neutral



    Indeed it does - which might not be a safe assumption since some older 3-phase systems employed a half-sized N. So if you happen to be on the end of an old 3-phase cable where only one phase is significantly used and no parallel paths with N you could see two-thirds of the v.d. along N instead of half - so maybe 24.53V might be closer in some cases.