Swa clipped with plastic cleats found during condition report.

Found the above on the wall of a pub beer garden during an inspection.It runs horizontally 2m above ffl.

Was going to give it a C3,but a friend thought it has to be fixed asap.Wondered what people on here thought.

                                                                                                                                            Regards,Hz
Parents
  • For my money I'd say C3 if it could fall across an escape route (comparable to an indoor socket without 30mA RCD protection to my mind) - but if it would just hang a little lower on the wall or fall to the ground at the foot of the wall and not get in anybody's way during a fire, then a just note at most - no code (doesn't comply but doesn't pose a danger - code 4 in old money).


       - Andy.
Reply
  • For my money I'd say C3 if it could fall across an escape route (comparable to an indoor socket without 30mA RCD protection to my mind) - but if it would just hang a little lower on the wall or fall to the ground at the foot of the wall and not get in anybody's way during a fire, then a just note at most - no code (doesn't comply but doesn't pose a danger - code 4 in old money).