Service cable and cut out too hot.

I was called by a local hospice to investigate "overheating" and found the DNO service cable and cut out to be alarmingly hot, I would estimate the surface temperature of the service cable to be at least 60 degrees. Definite smell of hot PVC.

Enquires suggested that the supply was originally 60 amps, single phase and was upgraded to 100 amps by fitting a larger fuse.


Measured load was just just under 100 amps, it probably exceeded 100 amps if anyone used a kettle.Service cable looks like only about 10mm. Voltage is rather low at 221 volts, but just within tolerance.


Is it worth calling the DNO, or will they simply say "supply working, do not worry" I suspect that the service cable is very undersized, but am aware that DNOs work to different rules.


I have moved combustibles away from the cable and advised reducing the load a bit,


Parents
  • Former Community Member
    0 Former Community Member
    There should be 100 amps available continually, as the supply capacity is stated as 23KVA


    Odd that this is stated on a bill for single-phase.


    Regards


    BOD
Reply
  • Former Community Member
    0 Former Community Member
    There should be 100 amps available continually, as the supply capacity is stated as 23KVA


    Odd that this is stated on a bill for single-phase.


    Regards


    BOD