Well, my understanding is that DNOs have to upgrade the supply to 100 A on request, meaning that 25 mm2 or 35 mm2 tails would be required (and a 100 A CU and main switch). If you are fitting a 100 A CU, why not fit tails to suit - regardless of the maximum demand today, the consumer may want an EV charging point fitted tomorrow.
gkenyon:
Well, my understanding is that DNOs have to upgrade the supply to 100 A on request, meaning that 25 mm2 or 35 mm2 tails would be required (and a 100 A CU and main switch). If you are fitting a 100 A CU, why not fit tails to suit - regardless of the maximum demand today, the consumer may want an EV charging point fitted tomorrow.