CONSUMERS TAILS IN THE OSG

I have just been having a scan read of the latest edition of the OSG. On page 20 it says in respect of consumers tails, " Polarity should be indicated by the colour of the insulation and the minimum cable size should be 25mm".


Alongside this statement is a reference to 514.3.1. I am OK with the requirement in 514.3.1 for the colour of the insulation but where  does the requirement come from for the CSA to be 25mm?


I do know some DNOs representatives may require a minimum CSA of 25mm but I suspect that this is a personal preference. My thinking is this is one of the myths and legends of electrical installation work that has been repeated so often that it has become fact. My view is the tails need to be sized to take the maximum load and they also need to be co-coordinated with the supply fuse. In addition some older consumer unit terminals will not take a 25mm tail.


Can anyone direct me to a reference source that requires the minimum CSA of meter tails to be 25mm?


Parents

  • Sparkingchip:

    Three weeks ago I took sole responsibility for connecting the tails of the new installation that I had installed into the new suppliers meter, neither metering services or the DNO would have done it for me or taken responsibility if there had been a big flash and a bang.


    Had I chosen to install 16 mm tails rather than 25 mm tails, as far as I know no one would have stopped me from connecting them.


    Sometimes I think I’m in a parallel universe that looks the same, but where the rules of life are different.  


    Andy B.




    Probably a parallel universe created by Douglas Adams?


    Z.

Reply

  • Sparkingchip:

    Three weeks ago I took sole responsibility for connecting the tails of the new installation that I had installed into the new suppliers meter, neither metering services or the DNO would have done it for me or taken responsibility if there had been a big flash and a bang.


    Had I chosen to install 16 mm tails rather than 25 mm tails, as far as I know no one would have stopped me from connecting them.


    Sometimes I think I’m in a parallel universe that looks the same, but where the rules of life are different.  


    Andy B.




    Probably a parallel universe created by Douglas Adams?


    Z.

Children
No Data