Outstandng 18th Oddities

As far as I recall, we still have some unanswered questions about some of the changes in the 18th. Does anyone have any further information about these? (If not at least this post should ensure the issues aren't forgotten with the demise of the old Forum.)


From memory there was at least:


461.2
  1. The intended meaning of the phrase "neutral conductor is reliably connected to Earth by a low resistance to meet the disconnection times of the protective devices" (given that the Part 2 definition of "Earth" is conductive mass of the Earth rather than any protective conductor or MET; and which protective devices are we talking about anyway?)

  • Also "protective equipotential bonding is installed" - is this intended to mean it actually is installed, or is installed where it is required? (Otherwise new installations with plastic pipes would need N isolation everywhere)


531.3.6 - if it the intention to prohibit the use of Socket RCDs and similar (e.g. FCU RCDs) for additional protection? (being that the generally comply with BS 7288 etc which appears to have a slightly different set of technical requirements to the standards listed)


537.3.2 - Switching off for mechanical maintenance. Although the definition of mechanical maintenance remains unchanged - so continues to include simple relamping - the requirements have changed considerably to the point they just about require complete electrical isolation. Thus a common lightswitch is no longer suitable for switching off for replacing a domestic lamp. Was this really the intention? Or are the changes aimed more at rotating machinery? Given that most householders would prefer not to plunge and entire floor let alone the complete installation into darkness to replace a simple lamp, should we be installing switches rated for isolation in every room?


any others?


   - Andy.
Parents

  • Hi Andy I have just thought of an anommly, the 18th edition was the first DPC since the Internet started where the P did not stand for public, only those signed in members of the BSI website could view the draft. It made public comment very limited compared to previous publications



    I agree with Graham on that point - I'm not a member of the BSI but I had little difficulty submitting quite a list of comments on the 18th DPC. Yes, there's the hoop to jump though to register on the web site - but I don't recall that being at all difficult - and nothing you wouldn't expect on any other web site where you submitted comments.


    There was the hiccup with the new BSI system struggling to cope with the shear size of BS 7671 and the eventually the whole thing being made available as a PDF (which I can understand the BSI and IET being uncomfortable with from a copyright point of view), but we got there in the end. For me the bit about the new process I don't like is not being able to readily keep a copy of all my responses (for future reference) without a lot of tedious copying & pasting.


    I do think the DPC process does have some value. Remember Part 8 (energy efficiency) in the DPC? - which has so many things the designer had to 'take into consideration' that the process would add a huge amount of time to the simplest design and even then it would be entirely unclear whether the design actually met the requirements of BS 7671 or not. As far as I can tell, without all the negative comments on the DPC it would have remained a fundamental part of the regulations - rather than having being kicked into the long grass of appendix 17 where it can be safely ignored by most of us. I've noticed quite a few other changes that seem to have been the result of DPC comments over the years too.


    What would be nice though is some kind of feedback about why comments were apparently ignored (as some quite sensible sounding ones seem to have been - one of the advantages of the new BSI system is that you can see other people's comments as well as your own). Was it because the commenter had fundamentally mis-understood what the regulation was trying to achieve (in which case a clarification of the wording might be in order?) or did the committee basically agree but felt their hands were tied (e.g. in order to maintain compatibility with say IEC standards), or were unsure of the consequences of making the change (as it's been there for so many years no-one can remember the original problem it was meant to address) or was it a good point but the knock-on consequences would have been so wide ranging that there wasn't time to make the changes under the current edition but it might be considered in later major revisions.


      - Andy.
Reply

  • Hi Andy I have just thought of an anommly, the 18th edition was the first DPC since the Internet started where the P did not stand for public, only those signed in members of the BSI website could view the draft. It made public comment very limited compared to previous publications



    I agree with Graham on that point - I'm not a member of the BSI but I had little difficulty submitting quite a list of comments on the 18th DPC. Yes, there's the hoop to jump though to register on the web site - but I don't recall that being at all difficult - and nothing you wouldn't expect on any other web site where you submitted comments.


    There was the hiccup with the new BSI system struggling to cope with the shear size of BS 7671 and the eventually the whole thing being made available as a PDF (which I can understand the BSI and IET being uncomfortable with from a copyright point of view), but we got there in the end. For me the bit about the new process I don't like is not being able to readily keep a copy of all my responses (for future reference) without a lot of tedious copying & pasting.


    I do think the DPC process does have some value. Remember Part 8 (energy efficiency) in the DPC? - which has so many things the designer had to 'take into consideration' that the process would add a huge amount of time to the simplest design and even then it would be entirely unclear whether the design actually met the requirements of BS 7671 or not. As far as I can tell, without all the negative comments on the DPC it would have remained a fundamental part of the regulations - rather than having being kicked into the long grass of appendix 17 where it can be safely ignored by most of us. I've noticed quite a few other changes that seem to have been the result of DPC comments over the years too.


    What would be nice though is some kind of feedback about why comments were apparently ignored (as some quite sensible sounding ones seem to have been - one of the advantages of the new BSI system is that you can see other people's comments as well as your own). Was it because the commenter had fundamentally mis-understood what the regulation was trying to achieve (in which case a clarification of the wording might be in order?) or did the committee basically agree but felt their hands were tied (e.g. in order to maintain compatibility with say IEC standards), or were unsure of the consequences of making the change (as it's been there for so many years no-one can remember the original problem it was meant to address) or was it a good point but the knock-on consequences would have been so wide ranging that there wasn't time to make the changes under the current edition but it might be considered in later major revisions.


      - Andy.