Recently sat the 18th Edition Course and of the understanding EV Charging points shall be fed from a TT Supply. PME is acceptable only when feeding any other equipment ie Lamp posts Ticket Machines for example and providing Type A or Type B RCD is fitted and the Charger point is then to be separately spiked. Just looking on the attached and a company called Pod Point suggest TN-S is acceptable with no need for an earth spike. Wondered if anyone else has come across this diagram and can confirm TN-S is acceptable without the spike (see - page 2)
Nice write up by EV company, some good advice there. always best for supplies outside the equipotential zone to have an independent earth, but if we offer a separate earth return, and an example is a cable attached to an incoming supply sheath via a clip, this is ideal. Temporary builders supplies, which because an equipotential zone cannot be guaranteed are another example of using a separate earth return. So go ahead and feel free to use the facility.
Nice write up by EV company, some good advice there. always best for supplies outside the equipotential zone to have an independent earth, but if we offer a separate earth return, and an example is a cable attached to an incoming supply sheath via a clip, this is ideal. Temporary builders supplies, which because an equipotential zone cannot be guaranteed are another example of using a separate earth return. So go ahead and feel free to use the facility.