This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

Compliant?

Is this arrangement compliant or not?


Consumer unit. R.C.D. protected shower circuit supplied by a B40 M.C.B. which runs to a cord ceiling switch  in the shower room in 6.0mm2 T&E. Old electric shower removed. New power shower installed with water supplied from tanks. 0.63 Amp transformer in loft to feed new integral shower pump motor. Loft transformer fed via 3 Amp fused switched fused connection unit on a 1.0mm2 T&E cable from old shower ceiling cord switch. 1.0 mm2 T&E run 2.5 metres.


P.S. The switched fused connection unit is at the end of the supply cables.


Confirmation or condemnation by regs. please.


Z.
Parents
  • The easy fix is to avoid questions about the length of cable before the 3A fuse, is to change  the 40A breaker for something smaller - for a 3A fuse, almost anything would do, 6A, 10A 16A - whatever is available .
Reply
  • The easy fix is to avoid questions about the length of cable before the 3A fuse, is to change  the 40A breaker for something smaller - for a 3A fuse, almost anything would do, 6A, 10A 16A - whatever is available .
Children
No Data