Compliant?

Is this arrangement compliant or not?


Consumer unit. R.C.D. protected shower circuit supplied by a B40 M.C.B. which runs to a cord ceiling switch  in the shower room in 6.0mm2 T&E. Old electric shower removed. New power shower installed with water supplied from tanks. 0.63 Amp transformer in loft to feed new integral shower pump motor. Loft transformer fed via 3 Amp fused switched fused connection unit on a 1.0mm2 T&E cable from old shower ceiling cord switch. 1.0 mm2 T&E run 2.5 metres.


P.S. The switched fused connection unit is at the end of the supply cables.


Confirmation or condemnation by regs. please.


Z.
Parents
  • Yes Andy I was thinking of 434.2.1 (i) and (ii).


    (i) The 1.0mm2 not exceeding 3m in length.


    (ii) "Be installed in such a manner as to reduce the risk of fault to a minimum." The cable is inaccessible as it runs under a tank stand and out of reach or risk of being stood on or mechanically damaged. 


    (iii) Just what requirement is meant here? Run in metal containment perhaps?


    Z.
Reply
  • Yes Andy I was thinking of 434.2.1 (i) and (ii).


    (i) The 1.0mm2 not exceeding 3m in length.


    (ii) "Be installed in such a manner as to reduce the risk of fault to a minimum." The cable is inaccessible as it runs under a tank stand and out of reach or risk of being stood on or mechanically damaged. 


    (iii) Just what requirement is meant here? Run in metal containment perhaps?


    Z.