Compliant?

Is this arrangement compliant or not?


Consumer unit. R.C.D. protected shower circuit supplied by a B40 M.C.B. which runs to a cord ceiling switch  in the shower room in 6.0mm2 T&E. Old electric shower removed. New power shower installed with water supplied from tanks. 0.63 Amp transformer in loft to feed new integral shower pump motor. Loft transformer fed via 3 Amp fused switched fused connection unit on a 1.0mm2 T&E cable from old shower ceiling cord switch. 1.0 mm2 T&E run 2.5 metres.


P.S. The switched fused connection unit is at the end of the supply cables.


Confirmation or condemnation by regs. please.


Z.
Parents

  • Foffer:

    The cord switch terminals would not be suitable for 1mm cable. 134.1.4


    That is why the 1.0mm2 copper was trippled over at the terminals. The connections are fine.


    Z.




     

Reply

  • Foffer:

    The cord switch terminals would not be suitable for 1mm cable. 134.1.4


    That is why the 1.0mm2 copper was trippled over at the terminals. The connections are fine.