Just trying to get my head around regulation 536.4.202, particularly the last line.
“However overload protection shall not solely be based on the use of diversity factors of the downstream circuits. To achieve overload protection of RCCBs or switches, the rated current of the OCPD shall be selected according to the manufacturers instructions”.
If I understand it correctly in a the sum of the downstream MCBs should not exceed the current rating of the RCD. So in most dual RCD split load boards the RCDs would need to be rated at 100A
Is this correct, because there seem to be a lot of "pre-populated" boards still being sold with 63A RCDs?
How are others interpreting this new reg?