Board change

Former Community Member
Former Community Member
If a EICR has been carried out recently 4 weeks ago, if you change the board would you be required to carryout testing on all circuits or can you reference the EICR.
Parents

  • AJJewsbury:

    An insulation test certainly - even if it's just a global L+N to PE test on the completed board.




    I agree that an IR test is necessary, but completely messed up by USB sockets which have to be excluded, which is a particular problem in RFCs.

Reply

  • AJJewsbury:

    An insulation test certainly - even if it's just a global L+N to PE test on the completed board.




    I agree that an IR test is necessary, but completely messed up by USB sockets which have to be excluded, which is a particular problem in RFCs.