AJJewsbury:
An insulation test certainly - even if it's just a global L+N to PE test on the completed board.
Good grief, the new work is the DB change. The final circuits are not new.
Alcomax:
AJJewsbury:
No. Initial verification has been and gone. The fixed wiring [ the final circuits, the existing ones ] were installed and certified before you were there....at initial verification of the , then , new installation.
Humm, not quite. The previous initial verification didn't include your new work did it? And that's the bit you're issuing the certificate to cover. Certificates can't cover existing parts of installations - there are EICRs (reports, not certificates) for that.Yes, you have to do some verification when re-energising the circuits by virtue of DB replacement. But enough to demonstrate that things are no less safe than when you started.
You should be able to show that your new work complies entirely with current standards - and that the existing installation, where non compliant, is no less safe that it was before. You can't really skimp on the I&T of your new work.
- Andy.
Good grief, the new work is the DB change. The final circuits are not new.
Do the applicable parts of the inspection schedule appropriate to the changing of db.
AJJewsbury:
No. Initial verification has been and gone. The fixed wiring [ the final circuits, the existing ones ] were installed and certified before you were there....at initial verification of the , then , new installation.
Humm, not quite. The previous initial verification didn't include your new work did it? And that's the bit you're issuing the certificate to cover. Certificates can't cover existing parts of installations - there are EICRs (reports, not certificates) for that.Yes, you have to do some verification when re-energising the circuits by virtue of DB replacement. But enough to demonstrate that things are no less safe than when you started.
You should be able to show that your new work complies entirely with current standards - and that the existing installation, where non compliant, is no less safe that it was before. You can't really skimp on the I&T of your new work.
- Andy.
No. Initial verification has been and gone. The fixed wiring [ the final circuits, the existing ones ] were installed and certified before you were there....at initial verification of the , then , new installation.
Yes, you have to do some verification when re-energising the circuits by virtue of DB replacement. But enough to demonstrate that things are no less safe than when you started.
SScho:
but in the case of just a board replacement, it will not be for the purposes of initial verification.
I don't think you've quite understood... Where are you getting this information? You need to go over the process of initial verification when you change a board, exactly as you would when you have a brand new installation.
The Regs state that you shouldn't use a minor works certificate for a board change, and that you should use the Installation Certificate (with the schedule of inspections and schedule of test results.)
You need to go over the process of initial verification when you change a board, exactly as you would when you have a brand new installation.
in larger installations that would be impractical so you would almost certainly look for ways to limit the testing beyond what had been worked on
I agree Andy, but this should be accounted for at the initial pricing of the job and finding either a way to do this in a practical way, either at night or out of hours. The power has to go off anyway for the board to be changed over - I was preparing the bid for a few board changes at a hospital and it became rather complicated and we decided that it'd be wise to start testing things before we rip out the old board and replace with RCBO's so we could find the problems easier to start with and know what we were dealing with and not have to have the power off for longer than necessary. Anything that can't be tested after the installation of the new board should be noted down as a limitation with the details of said limitation recorded on a separate sheet.
For domestic situations, I'd recommend testing the entire thing as there shouldn't be anything stopping you from doing so. I wouldn't class it as a "new" installation for the entire thing, but under the "Description and extent of the installation" I'd definitely mention that the circuits tested are existing and that the only change is the new board, breakers and characteristics surrounding it.
- S
You need to go over the process of initial verification when you change a board, exactly as you would when you have a brand new installation.
but in the case of just a board replacement, it will not be for the purposes of initial verification.
I don't think you've quite understood... Where are you getting this information? You need to go over the process of initial verification when you change a board, exactly as you would when you have a brand new installation.
The Regs state that you shouldn't use a minor works certificate for a board change, and that you should use the Installation Certificate (with the schedule of inspections and schedule of test results.)
SScho:
Alcomax:
the circuits have been in use for around 30yrs .... It could be due a full re-wire if the circuits are that sort of age.
Why at the age of 30 is the wiring suspect enough to be condemned? Is this the "Logan's Run" approach to work generation?In my opinion, a board change requires a full test and classed as a new installation
A distribution board change is a replacement , and does not "renew the installation". A marketing ploy, maybe, for the unscrupulous.
I admit that there are installations that are still to be deemed as "OK", even though they could be 50 odd years old, but as I said, it depends entirely on the condition of the installation and part of the reason why I would want to do a full test on it to make sure nothing has broken down or is on the verge of it - Even though everyone loves going back to site 3 months down the line because the lights keep tripping and it was "your fault"...
As for my reasoning for a full test on a new DB - BS7671 specifies that a minor works certificate "should not be used for replacement of distribution boards or similar items" (appendix 6, page 466 - 18th Edition). So you're not doing a minor works certificate, and you're not doing a condition report - that whittles down the options a bit. (See Page 464 of BS7671 18th Edition IET Wiring Regulations) -ELECTRICAL INSTALLATION CERTIFICATE
Notes for the person producing the Certificate:
- The electrical Installation Certificate is to be used only for the initial certification of a new installation or for an addition or alteration to an existing installation where new circuits have been introduced, or the replacement of a consumer unit/distribution board.
You also need to confirm that the board you're supplying has the appropriate equipment for the supply characteristics and the correct operating and protective factors for the installation provided. Hardly a "marketing ploy" to make sure you're doing something properly.