in larger installations that would be impractical so you would almost certainly look for ways to limit the testing beyond what had been worked on
I agree Andy, but this should be accounted for at the initial pricing of the job and finding either a way to do this in a practical way, either at night or out of hours. The power has to go off anyway for the board to be changed over - I was preparing the bid for a few board changes at a hospital and it became rather complicated and we decided that it'd be wise to start testing things before we rip out the old board and replace with RCBO's so we could find the problems easier to start with and know what we were dealing with and not have to have the power off for longer than necessary. Anything that can't be tested after the installation of the new board should be noted down as a limitation with the details of said limitation recorded on a separate sheet.
For domestic situations, I'd recommend testing the entire thing as there shouldn't be anything stopping you from doing so. I wouldn't class it as a "new" installation for the entire thing, but under the "Description and extent of the installation" I'd definitely mention that the circuits tested are existing and that the only change is the new board, breakers and characteristics surrounding it.
- S
SScho:
but in the case of just a board replacement, it will not be for the purposes of initial verification.
I don't think you've quite understood... Where are you getting this information? You need to go over the process of initial verification when you change a board, exactly as you would when you have a brand new installation.
The Regs state that you shouldn't use a minor works certificate for a board change, and that you should use the Installation Certificate (with the schedule of inspections and schedule of test results.)
You need to go over the process of initial verification when you change a board, exactly as you would when you have a brand new installation.
No. Initial verification has been and gone. The fixed wiring [ the final circuits, the existing ones ] were installed and certified before you were there....at initial verification of the , then , new installation.
Yes, you have to do some verification when re-energising the circuits by virtue of DB replacement. But enough to demonstrate that things are no less safe than when you started.
AJJewsbury:
No. Initial verification has been and gone. The fixed wiring [ the final circuits, the existing ones ] were installed and certified before you were there....at initial verification of the , then , new installation.
Humm, not quite. The previous initial verification didn't include your new work did it? And that's the bit you're issuing the certificate to cover. Certificates can't cover existing parts of installations - there are EICRs (reports, not certificates) for that.Yes, you have to do some verification when re-energising the circuits by virtue of DB replacement. But enough to demonstrate that things are no less safe than when you started.
You should be able to show that your new work complies entirely with current standards - and that the existing installation, where non compliant, is no less safe that it was before. You can't really skimp on the I&T of your new work.
- Andy.
Alcomax:
AJJewsbury:
No. Initial verification has been and gone. The fixed wiring [ the final circuits, the existing ones ] were installed and certified before you were there....at initial verification of the , then , new installation.
Humm, not quite. The previous initial verification didn't include your new work did it? And that's the bit you're issuing the certificate to cover. Certificates can't cover existing parts of installations - there are EICRs (reports, not certificates) for that.Yes, you have to do some verification when re-energising the circuits by virtue of DB replacement. But enough to demonstrate that things are no less safe than when you started.
You should be able to show that your new work complies entirely with current standards - and that the existing installation, where non compliant, is no less safe that it was before. You can't really skimp on the I&T of your new work.
- Andy.
Good grief, the new work is the DB change. The final circuits are not new.
Do the applicable parts of the inspection schedule appropriate to the changing of db.
Good grief, the new work is the DB change. The final circuits are not new.
AJJewsbury:
An insulation test certainly - even if it's just a global L+N to PE test on the completed board.