R.C.D. tripping and earthing concerns.

Evnin' All,

                  I have had a hard day and my brain is in meltdown so please excuse nonsense and silliness.


I installed a new socket in a house today. TT earthing presumably. New A.B.C. overhead supply. Nearest D.N.O. P.M.E. pole earth rod about 15 metres away from the house. When I tested the R.C.D. it worked on the test button, but the switch seemed a bit graunchy. It would not trip off on 30mA test, but did trip off on the 5X R.C.D. test at a socket. I replaced the R.C.D. The same thing happened. No trip on 30mA test setting, but it did trip off on the 5X setting.


An earth fault loop test at a socket showed a reading of 185 Ohms.


A  length of 6.0mm2 green and yellow cable was found in the front yard but the electrode is not inspectable as it is covered by block paving is old. It may have rotted away. With the main switch off the resistance from N. to the earth bar in the consumer unit is about 180 Ohms. 


The consumer unit is a 10 way unit with just one 30mA R.C.D.


I converted the earthing to P.M.E. and then nuisance tripping was seen. I intend to install an all R.C.B.O. board tomorrow.


Sometimes a fridge when turned on will trip the R.C.D., other times it is a freezer, then the kettle. But the appliances test o.k. with an insulation resistance test. Once or twice the tungsten lighting circuits tripped off the R.C.D.


I assume that the addition of individual leakage current is responsible for the R.C.D. tripping, but there is no logic to which individual appliances/circuits seem to cause it. Two suspected rings test o.k. for insulation resistance.


The house owner reported that the gas fitter received a shock when doing something under the AGA. The main gas bond was loose at its clamp. I have replaced the earth clamp.


Any thoughts please?


EDIT. P.S. I have a Voltage tester that will trip off a 30mA R.C.D. if connected to the outgoing R.C.D. L. and E. at the same time. When this was connected to the original R.C.D's LIVE INCOMING terminal and the E. bar the R.C.D. tripped off. Did this raise the Voltage on the C.P.C.s sufficiently to trip off the RC.D?


Z.


Parents
  • Dear Mum they are treating me well here in Berwyn. I can even have my own personal cell key for privacy, but the screws have a master key. At least it is better than nothing. Some say that Berwyn is the cushiest hotel for people like me at her majesty's pleasure. I am studying lock picking at present in my spare time, and have joined a program to improve this place, I do gardening, painting and electrical work like bonding pipes. The old boy in the next cell is in for not having a t.v. licence, her is 97.


    Here is a video of the case that was heard before mine...

    https://www.youtube.com/watch?v=9VgwxKW0J6I


    P.S. Don't forget to feed the goldfish.


    Bye,

    love,


    3499875 Z.
Reply
  • Dear Mum they are treating me well here in Berwyn. I can even have my own personal cell key for privacy, but the screws have a master key. At least it is better than nothing. Some say that Berwyn is the cushiest hotel for people like me at her majesty's pleasure. I am studying lock picking at present in my spare time, and have joined a program to improve this place, I do gardening, painting and electrical work like bonding pipes. The old boy in the next cell is in for not having a t.v. licence, her is 97.


    Here is a video of the case that was heard before mine...

    https://www.youtube.com/watch?v=9VgwxKW0J6I


    P.S. Don't forget to feed the goldfish.


    Bye,

    love,


    3499875 Z.
Children
No Data