Connectors for 200V dc

I have an installation that uses 200V dc (balanced about earth but not earthed). All the installed equipment is direct wired, but I have an application that needs a plug and socket.  I don't want to use the standard connectors that are also used for ac to avoid ac equipment being plugged in inadvertently.  The equipment in question will draw a current around 8 amps and is metal framed, not double insulated so needs an earth.  I would be grateful for any suggestions/ advice.


I am sure that this has been discussed previously, but I cannot find it on the old forum.


Many thanks,


David
Parents
  • I would avoid the Schuko if possible, you may not have anything else on site that fits but a visiting European may find it the perfect place for his/her Europlug wallwart charger. Probably ok if it is a switchmode unit, not ok if it has a transformer.


    A few years ago Conrad, a German Maplin/RS, was offering BS1363 plugs and sockets for 12V caravan use. Ok until you holiday in the UK.


    Best regards


    Roger