Connectors for 200V dc

I have an installation that uses 200V dc (balanced about earth but not earthed). All the installed equipment is direct wired, but I have an application that needs a plug and socket.  I don't want to use the standard connectors that are also used for ac to avoid ac equipment being plugged in inadvertently.  The equipment in question will draw a current around 8 amps and is metal framed, not double insulated so needs an earth.  I would be grateful for any suggestions/ advice.


I am sure that this has been discussed previously, but I cannot find it on the old forum.


Many thanks,


David
Parents
  • Yes, Mike , I do remember the thread, and have posted several others when it seemed useful to have an opinion on unusual situations from the expertise here.  Thanks for the suggestion of the Buccaneers, which look ideal in this situation.


    David
Reply
  • Yes, Mike , I do remember the thread, and have posted several others when it seemed useful to have an opinion on unusual situations from the expertise here.  Thanks for the suggestion of the Buccaneers, which look ideal in this situation.


    David