"potentially dangerous" or improvement required re: missing covers on conduit inspection fittings

Taking in to account the guided definition of "potentially dangerous" and any IP rating compromise (and loss of mechanical protection):


If I proffered that missing covers/lids from a steel conduit inspection fittings was not worthy of being described as potentially dangerous, would you agree, or argue it was ?


Would you be persuaded one way or the other depending on the 'accessibility' factor ?


My take: if its out of the way from fingers etc, then i'd say not potentially dangerous. If it was readily accessible for touch/impact, then I would be thinking otherwise.


Reading back on some [I think] well known guidance regarding periodic inspections, there is a bit regarding where cable sheathing is not taken into an enclosure leaving the basic protected conductors exposed to touch; in some conditions it is considered as not "potentially dangerous" but only requiring "improvement" and from past threads this has provoked some interesting debate and opinions; is there a difference from these situations to the above missing lids question (or even indeed trunking lid missing or unused cable access holes in trunking) ?


Hope you are all keeping well and enjoying the 'new' forum ! :-)

Cheers

Habs
Parents

  • psychicwarrior:

    If I proffered that missing covers/lids from a steel conduit inspection fittings was not worthy of being described as potentially dangerous, would you agree, or argue it was ?




    I wouldn't be too happy with missing covers from outdoor BESA boxes because water would almost certainly get in and damage the wiring. However, unless (as mapj1 has suggested) there be junctions in the BESA boxes (or other enclosures) I cannot see any immediate threat, so provided that it is indoors, C3 for me.


    If all it requires is lids, remediation is hardly difficult.

Reply

  • psychicwarrior:

    If I proffered that missing covers/lids from a steel conduit inspection fittings was not worthy of being described as potentially dangerous, would you agree, or argue it was ?




    I wouldn't be too happy with missing covers from outdoor BESA boxes because water would almost certainly get in and damage the wiring. However, unless (as mapj1 has suggested) there be junctions in the BESA boxes (or other enclosures) I cannot see any immediate threat, so provided that it is indoors, C3 for me.


    If all it requires is lids, remediation is hardly difficult.