"potentially dangerous" or improvement required re: missing covers on conduit inspection fittings

Taking in to account the guided definition of "potentially dangerous" and any IP rating compromise (and loss of mechanical protection):


If I proffered that missing covers/lids from a steel conduit inspection fittings was not worthy of being described as potentially dangerous, would you agree, or argue it was ?


Would you be persuaded one way or the other depending on the 'accessibility' factor ?


My take: if its out of the way from fingers etc, then i'd say not potentially dangerous. If it was readily accessible for touch/impact, then I would be thinking otherwise.


Reading back on some [I think] well known guidance regarding periodic inspections, there is a bit regarding where cable sheathing is not taken into an enclosure leaving the basic protected conductors exposed to touch; in some conditions it is considered as not "potentially dangerous" but only requiring "improvement" and from past threads this has provoked some interesting debate and opinions; is there a difference from these situations to the above missing lids question (or even indeed trunking lid missing or unused cable access holes in trunking) ?


Hope you are all keeping well and enjoying the 'new' forum ! :-)

Cheers

Habs
Parents
  • I would Code 2 for the main reason that the covers are more likely to be reinstated plus single insulation shouldn’t be on show, it’s one of my pet hates especially on meter tails. Plus never a good sign when lids are missing especially trunking, normally means someone has taken little care working on the installation.
Reply
  • I would Code 2 for the main reason that the covers are more likely to be reinstated plus single insulation shouldn’t be on show, it’s one of my pet hates especially on meter tails. Plus never a good sign when lids are missing especially trunking, normally means someone has taken little care working on the installation.