Visual assessment of existing installation earthing arrangement.

3074669d439044522977d61280a3596e-huge-20190417_131736.jpg

Go on, make a quick decision as to what the earthing arrangement is.


Andy
Parents
  • 3 wires come into the building.from the outside, and so I would have said TN-S overhead or TT split phases  but mostly  I think TNS.

    Though maybe not clear as it looks like either something odd has been done with the earths and neutral at the cut-out, or more likely  that all 3 wires LNE duck down behind the board to supply another cut-out on the other side of the wall as a loop through supply.

    Hopefully there is not an un-needed NE link or an NE transposition, unless this is an odd way of implementing a double fault to failure on TNS upgraded to  PEN.


    Now the pole will be L1/L2/L3/N /E and presumably the 'spare' is a street lighting timed live, so that supports a TN-S assuming it has not been retrospectively PME'd.

Reply
  • 3 wires come into the building.from the outside, and so I would have said TN-S overhead or TT split phases  but mostly  I think TNS.

    Though maybe not clear as it looks like either something odd has been done with the earths and neutral at the cut-out, or more likely  that all 3 wires LNE duck down behind the board to supply another cut-out on the other side of the wall as a loop through supply.

    Hopefully there is not an un-needed NE link or an NE transposition, unless this is an odd way of implementing a double fault to failure on TNS upgraded to  PEN.


    Now the pole will be L1/L2/L3/N /E and presumably the 'spare' is a street lighting timed live, so that supports a TN-S assuming it has not been retrospectively PME'd.