ENA Engineering Recommendation G12 published by the Energy Networks Association
ENA Engineering Recommendation G12 Issue 4 Amendment 1 December 2015 Requirements for the Application of Protective Multiple Earthing to Low Voltage Networks contains clause 5.2.1 which states:
Provision of earth terminal requires that where a metallic gas service is provided to a consumer’s premises with a PME earth terminal, an insulated insert should be fitted in the gas service.
HistoricalnotefromENA:
Prior to these standards (in particular IGEM GL/5), IJs were occasionally installed downstream of the ECV. This was to comply with PME requirements, and so these IJs are still required.
IGEM/G/5 Edition 2 document published by the Institution of Gas Engineers and Managers
IGEM/G/5 Edition 2 document (clause 11.2) contains requirements for insulating fittings. Clause 11.2.1 states:
… insulating fittings shall be installed in all metal pipe, whether gas carrying or containing a PE liner, capable of providing electrical continuity between earth and the above ground pipework.
Clause 11.2.2 states:
Insulation fittings shall be installed in accessible location as close to the pipes entry into the building or, in the case of external pipework, as close as possible to the pipes exit to the ground and upstream of any ECV. The uninsulated section of the exposed pipe shall be as short as possible.
Now by saying it has to be before the ECV, and therefore before the gas meter, it is not in the remit of Gas Safe, but Transco - who on the transmission and distribution side of things are allowed to use plastic pipes and fittings.
Plastic pipe and fittings after the meter would be considered a big 'no',, and is probably what the Gas Safe chaps are thnking of when they say they can't do it.
Sometimes referred to as a monolithic insulating joint or 'MIJ' by some maker's literature.
ENA Engineering Recommendation G12 published by the Energy Networks Association
ENA Engineering Recommendation G12 Issue 4 Amendment 1 December 2015 Requirements for the Application of Protective Multiple Earthing to Low Voltage Networks contains clause 5.2.1 which states:
Provision of earth terminal requires that where a metallic gas service is provided to a consumer’s premises with a PME earth terminal, an insulated insert should be fitted in the gas service.
HistoricalnotefromENA:
Prior to these standards (in particular IGEM GL/5), IJs were occasionally installed downstream of the ECV. This was to comply with PME requirements, and so these IJs are still required.
IGEM/G/5 Edition 2 document published by the Institution of Gas Engineers and Managers
IGEM/G/5 Edition 2 document (clause 11.2) contains requirements for insulating fittings. Clause 11.2.1 states:
… insulating fittings shall be installed in all metal pipe, whether gas carrying or containing a PE liner, capable of providing electrical continuity between earth and the above ground pipework.
Clause 11.2.2 states:
Insulation fittings shall be installed in accessible location as close to the pipes entry into the building or, in the case of external pipework, as close as possible to the pipes exit to the ground and upstream of any ECV. The uninsulated section of the exposed pipe shall be as short as possible.
Now by saying it has to be before the ECV, and therefore before the gas meter, it is not in the remit of Gas Safe, but Transco - who on the transmission and distribution side of things are allowed to use plastic pipes and fittings.
Plastic pipe and fittings after the meter would be considered a big 'no',, and is probably what the Gas Safe chaps are thnking of when they say they can't do it.
Sometimes referred to as a monolithic insulating joint or 'MIJ' by some maker's literature.