How to calculate transformer KVA

If you have a transformer with let's say 3x 400 amp fuses protecting its LV outgoing cables how do I calculate its KVA? Do you just time amps by the single phase voltage or by the volts across 2 phases
  • If you know the rated LV current (I) then for a three-phase transformer it would be I x Vln x 3 where Vln is the phase-neutral current, or I x Ipn x sqrt(3) where Vpn is the phase-phase current so 400A would imply 276kVA....


    ... But the fuse may or may not be directly related to the rating of the transformer, depending on what it's been put there by the designer for. They might well suggest a higher rating than the transformer actually is if they're only there for fault protection, for example, with overload dealt with by other means.


    It should be pretty obvious from the nameplate though, which if you can see the fuses you should be able to see!
  • Thanks jam that's a nice easy to work out way to do it. The reason for my question is simple curiousity
  • Hello Kelly, you might find this video interesting.

    https://www.youtube.com/watch?v=rp1OdR7fFGI


    Z.
  • Yes that video was good took a few minutes to get used to that guys accent but was very informative
  • Former Community Member
    0 Former Community Member
    You can make a rough estimation by doing the following calculation:


    First of all the following information should be available.


    a) Type of LV fuse (HRC/ Wired/Glass fuse)

    b) Voltage rating of LV. If the same is not available you can take the working voltage of LV winding as voltage rating. If this is not possible then see the fuse, generally they also have rated voltage printed on it. 

    c) Percentage impedance of transformer


    Calculation:


    In general, the fuses have a rating between 125% to 250% of the rated current of the LV winding. If you want a conservative estimation of transformer VA, you may assume that the fuse you have in hand is 250% of rating. Hence rated current can be estimated as 400/2.5  A. With voltage data available you can calculate the VA rating using standard formula.


    Please note this is a rough estimation as a number of factors such as whether the transformer has tap changer or has multiple windings etc shall affect the calculation.

    Hope this is of some help.


  • That's interesting I will use both suggested methods hopefully both will come up with similar results  il post when I've done it
  • Former Community Member
    0 Former Community Member
    Rated current of the LV winding, Rated voltage of the LV winding and Apparent power of three phase transformers are components of the following formula: S= √3 x Ur x Ir

    Usually everything happens the other way around: active power [P in kW] and power factor [cos] of the summarized load is known, it allows to find apparent power of the transformer [S in kVA] and then we can calculate the rated current of the LV winding. [when choosing a real  transformer, power is always taken with a reserve]

    But in you case, if you know the rated voltage of the LV winding [for example 415V phase-to-phase] then the question is - how do the rated current of the transformer and the main protection device on LV side correlate?
    I propose to assume that the rated current of the LV winding is not less than nominal current protection device, so   S =  1.732 x 415V x 400A =~ 300kVA