Wiring 10 vector heaters supplied by 10mm cable.

Former Community Member
Former Community Member
Hi,


Whilst on site a few weeks ago, I noticed an electrician wired 10 vector heaters onto a 10 gangway switch.

​​​​each of the switches turned each of the heater's on. 

however, all these switches were supplied by the 10mm cable I was running above the ceiling tiles. 

Now I noticed each heater had a power rating of 2500 watts, 


So assuming all the heater's were turned on, and given the kind of premises it was, all the heater's would be on if used, that would have been a total of 25000 watts supplied by a 10mm cable. 


I'm just confused as to how he wired it,

Im pretty sure they were wired parralel, as each heater had it's own flex going straight to the switch board. Can anyone can help with a wiring diagram. It's really been bugging me.
Parents
  • Former Community Member
    0 Former Community Member
    Initially, I thought this was something new I could learn, that's why I was asking for a wiring diagram. But like you said I was a bit concerned. I think now, seeing multiple comments, I can't really tell until I actually open it up and see, which is not going to happen.


    The cable was a 10mm twin and earth,

    Thanks everyone for your input, I have learnt something new from most of the comments.
Reply
  • Former Community Member
    0 Former Community Member
    Initially, I thought this was something new I could learn, that's why I was asking for a wiring diagram. But like you said I was a bit concerned. I think now, seeing multiple comments, I can't really tell until I actually open it up and see, which is not going to happen.


    The cable was a 10mm twin and earth,

    Thanks everyone for your input, I have learnt something new from most of the comments.