Type D MCB 5 Second Tripping Current

Former Community Member
Former Community Member
In BS 7671 17th Edition A3 table 41.3 for type D MCBs gives a 5 second tripping current as 230 x 0.95 / (10In).


When cross referencing time current graphs for type D MCBs I do not get a value of 10In for a 5 second tripping time.


For example see ABB time current graph below giving a current of around 16In for a 5 second trip time.


What is the reason for the difference in values when comparing type D MCB time current charts and table 41.3 in BS 7671 17th Edition A3 for 5 second trip times?

3e6afca19b11a5e876e17f88e8258582-huge-type-d.png
f5deabd80c6b55bd27c69795fb1b7c94-huge-20190722_083103.jpg

Parents
  • Former Community Member
    0 Former Community Member
    I'd go along with that - with sensible margins adopted, it would be a foolproof method of showing compliance with 0.4 and 5 second disconnections, based on data already required in BS EN 60898-1 - but we have something very similar with limiting Zs values so it may well not warrant the change of approach


    Regards


    OMS
Reply
  • Former Community Member
    0 Former Community Member
    I'd go along with that - with sensible margins adopted, it would be a foolproof method of showing compliance with 0.4 and 5 second disconnections, based on data already required in BS EN 60898-1 - but we have something very similar with limiting Zs values so it may well not warrant the change of approach


    Regards


    OMS