Insulation Resistance Testing

Hi,


I work as a Maintenance Electrician and part of my Testing role is to complete Insulation resistance testing on Supply cables between Metal cabinets on Highways Equipment - Normally Armoured or similar.


I have had 2391 since 2006 and at no point in my Testing Course did i ever come across something a colleague of mine seems to be insisting we all do. That is "Conductor to Ground Testing". I have in the past completed Phase to Neutral, Neutral to Earth and Earth to Phase and recorded these on my test certificates (All supplies are single phase). As far as I know there is nowhere to record such tests on any software or sheets I have seen. Am I missing something fairly obvious or does this seem pointless to others too? 


Regards Chivs
Parents
  • I often test the armour of an SWA to real earth (screwdriver in grass) to test for the integrity of the sheathing. I agree with Lyle and cannot see the point of the test with the cabinet earth disconnected unless there is a low resistance live to earth when you would want to find out if it is the cable or the cabinet.


    Perhaps a sensitively phrased question to determine the purpose?
Reply
  • I often test the armour of an SWA to real earth (screwdriver in grass) to test for the integrity of the sheathing. I agree with Lyle and cannot see the point of the test with the cabinet earth disconnected unless there is a low resistance live to earth when you would want to find out if it is the cable or the cabinet.


    Perhaps a sensitively phrased question to determine the purpose?