John Peckham:
Contrary to common belief supplementary protective equipotential bonding is still required in bathrooms, see Regulation 7091.415.2.
However it may be omitted IF where all 3 of the conditions set out in 701.415.2 are met. And where necessary a test has been carried out to prove compliance with 415.2.2.
The big question is can you omit the supplementary bonding in the "location" (the bathroom) if there is no main bonding as it is not required?
The assumption is there is a radiator present, which would be bonded together with the bath and any other metalwork. But we know that don't we, its been in the regs for 50 years.
The old bath was bonded back to the terminal block by main consumer unit over 6mm earth cable via the airing cupboard.
UKPN:
Working on the basis that various posters don't know the difference between bonding and earthing, I would go for bonding the bath. Take a 4mm back to the airing cupboard. Then you will sleep at night. If you take any notice of the 18th guide book you won't bond anything. (Although it's been saying bond everything for 50 years)