Electric Shock from Old P.I.R. Floodlight.

Today I was asked to investigate why an old outside P.I.R. tungsten halogen floodlight did not work. It had been installed on a 70s holiday chalet. The owner had installed it himself and admitted that he did not know much about electrics. I used my aluminium ladder to access it, the ladder has plastic feet and it stood on a concrete surface. When I went up to the floodlight my Voltstick suggested that the supply cable was dead. But when I touched the fitting I got a shock, this before I had removed the terminal box  cover. Anyway, after turning off at the consumer unit I noticed that the owner had fitted the live supply wire into the earth terminal. That was the cause of the shock I imagined. Anyway I removed the old floodlight and was going to fit a new L.E.D. one. I tested at the supply cable but there was no supply. All M.C.B.s were on and the R.C.D. was on as well. So how did I get a shock if the supply cable was dead? A charged capacitor perhaps? Or induced Voltage? No switch was found that controlled this cable.


I got a reading of about 2 Volts from the main P.M.E. earth terminal and a temporary earth rod bashed into the lawn.


There are three 11kV overheads about 30 metres away from this chalet.


Any ideas please?


Z.
Parents
  • I think you got a shock because of voltage on the earth lead you said you saw around 2 volts between the PME Earth and a lawn earth well what's to say that when you went up the ladder there wasn't  more on it if for instance the owner was cooking something or the immersion heater was on causing more voltage on the CNE wire




Reply
  • I think you got a shock because of voltage on the earth lead you said you saw around 2 volts between the PME Earth and a lawn earth well what's to say that when you went up the ladder there wasn't  more on it if for instance the owner was cooking something or the immersion heater was on causing more voltage on the CNE wire




Children
No Data