Neutral Point of Heater Bank

Hi,

I have an application to control a bank of resistive heating elements (52Kw) in a Star configuration from a Eurotherm Power Management unit to control heat output.

Is it standard practice to connect the Neutral Point to Neutral ?
Parents
  • In that situation the motor has failed and will probably require a rewind - further failures in the winding do not change that. 


    If heaters are connected in banks and one element in the bank fails then a replacement element would return the heater to full capacity.  The omission of a  neutral on this type of load can cause the failure of the whole bank as the voltage rise will stress the remaining elements.  If a neutral is connected the voltage will remain stable and further failures due to voltage stress would not occur.


    This is not a safety issue and is not AFAIK the subject of any regulation - however, the heaters I mentioned were replaced because the manufacturer accepted that the method of installation contributed to premature failure.


    Regards


    Geoff Blackwell
Reply
  • In that situation the motor has failed and will probably require a rewind - further failures in the winding do not change that. 


    If heaters are connected in banks and one element in the bank fails then a replacement element would return the heater to full capacity.  The omission of a  neutral on this type of load can cause the failure of the whole bank as the voltage rise will stress the remaining elements.  If a neutral is connected the voltage will remain stable and further failures due to voltage stress would not occur.


    This is not a safety issue and is not AFAIK the subject of any regulation - however, the heaters I mentioned were replaced because the manufacturer accepted that the method of installation contributed to premature failure.


    Regards


    Geoff Blackwell