IP rated luminaires for jet wash with high temp. water?

Evening all.


Bit of a head scratcher:


IP65 / IP66 testing must use water that it within 5K of the specimen under test.

IP69 testing uses water at 80ºC (+/- 5ºC).


I have a process area that will be subject to jet washing with hot water fed from the domestic system and so will be somewhere in the region of 40ºC - 60ºC.


The luminaires within the space shall be IP66 for the water flow rates but should they also be IP69 rated to account for the hot water?


Appreciate any thoughts.


P
Parents
  • temp is not the only factor, but also the strength of the jet.


    IP66 is 'jets of water' but only at approx 1 atmosphere pressure, and IP65 is 1/3 of that pressure.

    IP 69 is indeed hot but also at 100 atmosphere water pressure.

    It all rather depends on the strength of the jetwash, many are well above 1 atmosphere  IP 65/66 may not be quite enough if yours is one of these.


    IP69 ( or 69K in the German version of the standards  ) is common in places like aspects of food production that need more than just a light wash down.


    (Or ask the maker of the lights)
Reply
  • temp is not the only factor, but also the strength of the jet.


    IP66 is 'jets of water' but only at approx 1 atmosphere pressure, and IP65 is 1/3 of that pressure.

    IP 69 is indeed hot but also at 100 atmosphere water pressure.

    It all rather depends on the strength of the jetwash, many are well above 1 atmosphere  IP 65/66 may not be quite enough if yours is one of these.


    IP69 ( or 69K in the German version of the standards  ) is common in places like aspects of food production that need more than just a light wash down.


    (Or ask the maker of the lights)
Children
No Data