Rotary Isolators on ring circuit

Hello, I am dealing with an office refurb and existing installation consisting of about 8 rotary isolators on a ring circuit wired with 2.5mm2 singles and fed by BS88 32Amp fuse. From as builts it appears isolators supposed to serve power poles which appears were never installed, but I would like to reuse the existing circuit to feed new HRU - about 3Amp 1ph supply. Do I need to change the circuit to radial/replace isolators with fused spurs or can I reuse one of the existing isolator? I feel I can't use the isolators but doubt arose in me when my boss said that he thinks using isolators is compliant with BS. Please let me know, thank you :)
Parents
  • Wiring route is obvious, however there is no RCD protection as this was installed back in early 00s. For obvious reasons I don't want a mechanical fan on an RCD circuit especially that it's fed off from the fuseboard rather than a standard DB. 


    But from isolators point of perspective is it okay to have isolators on a ring rather than a twin sockets or a fused spur? Appendix 15 of BS7671 doesn't say anything about anything else than TSSO and spurs.
Reply
  • Wiring route is obvious, however there is no RCD protection as this was installed back in early 00s. For obvious reasons I don't want a mechanical fan on an RCD circuit especially that it's fed off from the fuseboard rather than a standard DB. 


    But from isolators point of perspective is it okay to have isolators on a ring rather than a twin sockets or a fused spur? Appendix 15 of BS7671 doesn't say anything about anything else than TSSO and spurs.