Passing cables through joists

I know that this has been discussed in the old forum, but I have been pondering the subject over the past couple of days.


I am more than happy to respect the exclusion zones at the ends and in the middle of joists (Electrician's Guide to the Building Regulations); but it seems odd that cables which are passed through joists must go through notches in the zone between 0.07 - 0.25 times the span, and holes in the 0.25 - 0.40 zone.


In essence, despite the removal of a substantial amount of material, the upper joist in my diagram is acceptable, but the 16 mm hole in the lower one is not.

6023a2338ff6952232f44f2cc4478e57-huge-20190802joist.jpg


It seems to me that any risk to the cable is much lower in holes than notches; and of course, if plumbers have already occupied the notch zone, there isn't much choice.


In order to remove and replace cablies descending to sockets below, I need to lift the second board in from the wall; but it would be a real PITA to have to lift another board (especially if tongue and groove) closer to the centre of the room particularly because there isn't much working space unless the furniture is removed.


I have no intention of placing holes below notches, but will the house fall down if I don't follow the Guide? ?
Parents
  • Almost certainly nothing will fall, unless it was already so marginal as to be dangerous.

    The top of the joist is in compression, and more so in the middle, and the bottom of the joist is in tension. So notching in the middle is bad, and is relegated to the edges. Clearly the top of the joist does nothing over the support, and all the load is born on the bottom, so cutting material nearer the bottom half of the joist is a no-no near the supports. In cases where a lot had to be removed, we have put another section of joist along side, and bolted and glued. This does not look like that case.

    Far more care is needed with the modern joist that is a blade of plywood and 2 roof battens, than the old fashioned solid kind, which has quite a lot of excess strength.
Reply
  • Almost certainly nothing will fall, unless it was already so marginal as to be dangerous.

    The top of the joist is in compression, and more so in the middle, and the bottom of the joist is in tension. So notching in the middle is bad, and is relegated to the edges. Clearly the top of the joist does nothing over the support, and all the load is born on the bottom, so cutting material nearer the bottom half of the joist is a no-no near the supports. In cases where a lot had to be removed, we have put another section of joist along side, and bolted and glued. This does not look like that case.

    Far more care is needed with the modern joist that is a blade of plywood and 2 roof battens, than the old fashioned solid kind, which has quite a lot of excess strength.