AJJewsbury:
A few subtleties to consider...There is nothing to stop you fitting a light bulb to a 100A circuit as long as the cable can withstand the possible short circuit condition.
If by a "light bulb" you mean something that fits into a the the usual sizes of BC or ES lampholders, then BS 7671 stipulates a maximum of 16A (559.5.1.204).
Could you have a 20A/1.5sq.mm. (method C) lawn mower circuit with some lights on it?
You might also have to consider the (probably 6A rated) lightswitches on the circuit as well as the cables - even though they're not in the path to the lawnmower (or whatever) they and so overload isn't a worry, the still need to be protected from faults, using a higher rated OPD could undermine that. The rewritten section 536 in the 18th makes that requirement more explicit that it used to be.
- Andy.
AJJewsbury:
A few subtleties to consider...There is nothing to stop you fitting a light bulb to a 100A circuit as long as the cable can withstand the possible short circuit condition.
If by a "light bulb" you mean something that fits into a the the usual sizes of BC or ES lampholders, then BS 7671 stipulates a maximum of 16A (559.5.1.204).
Could you have a 20A/1.5sq.mm. (method C) lawn mower circuit with some lights on it?
You might also have to consider the (probably 6A rated) lightswitches on the circuit as well as the cables - even though they're not in the path to the lawnmower (or whatever) they and so overload isn't a worry, the still need to be protected from faults, using a higher rated OPD could undermine that. The rewritten section 536 in the 18th makes that requirement more explicit that it used to be.
- Andy.