Underfloor Bus Bar Systems

The Definition in the Regulations for a Socket states " A Device, provided with Female Contacts, which is intended to be installed with the fixed wiring, and intended to receive a plug. A Luminaire track system is not regarded as a socket-outlet system"

From the above it would be my understanding that the Tap-Offs on an underfloor Bus Bar system are considered to be sockets. The exclusion of Luminaire track systems also appears to support this viewpoint as it infers that power Underfloor Bus Bar should be classed as sockets.
Parents
  • From a practical perspective, the thing about a socket outlet is that any unskilled person can plug in any old piece of junk (e.g. lawnmower with frayed flex), which the designer has no control over. So you want the socket RCD protected. For fixed equipment, the designer has more control: they get to choose what's wired into the FCU, and how well the flex is protected etc.


    So, if cleaning staff are turning up and plugging random industrial-sized portable cleaning equipment into your bus bar, you might want RCD protection. On the other hand if only a small selection of skilled staff are authorised / have access to the bus bar, and they know when to include an RCD with the equipment, then the bus bar shouldn't need RCD protection.


    Whether BS 7671 agrees with that is of course a separate matter.
Reply
  • From a practical perspective, the thing about a socket outlet is that any unskilled person can plug in any old piece of junk (e.g. lawnmower with frayed flex), which the designer has no control over. So you want the socket RCD protected. For fixed equipment, the designer has more control: they get to choose what's wired into the FCU, and how well the flex is protected etc.


    So, if cleaning staff are turning up and plugging random industrial-sized portable cleaning equipment into your bus bar, you might want RCD protection. On the other hand if only a small selection of skilled staff are authorised / have access to the bus bar, and they know when to include an RCD with the equipment, then the bus bar shouldn't need RCD protection.


    Whether BS 7671 agrees with that is of course a separate matter.