I am doing domestic electrical condition reports on Council properties and i am coming across earth clamps on incoming cable to provide means of earth.
I used to coded as cat 2 but the side manager says must be cat3 because he contacted the local REC (Western Power) and they do not want to know.
My other point with the REC's is that when they fit a new smart meter they suppose to fit an isolator/one shot too. Must be a local isolation.
MHRestorations:
Just an addon to further confirm what Kelly said, it very much depends on the DNO. My local DNO, (and Kelly's), [SSE], are particularly helpful and will respond typically within hours of a call about inadequate earthing on a TN-S supply. They still seem to install the 2 part brass clamps and supply a 10 or 16mm tail to whatever MET is available. (they will install a MET block if one is not there, they will NOT interfere with a customer's installation, of course)
I guess this may depend on area though, we work mostly in Gosport and the TN-S cables seem to be in fair condition. I guess a new service head is more time for them, so if Ze is okay, a new earth clamp is cheap and cheerful?
Anything more than that however, such as moving a service, and they'll install a TN-C-S head, and make the splice on the concentric outside the property.