IET announces new amendment to BS 7671 (IET Wiring Regulations)

Hi all


Just read about this in the latest edition of Wiring Matters Magazine and thought it may be of interest!
Parents
  • The NICEIC, ECA and ELECSA disagree.


    When the 17th Edition (BS 7671: 2008) was published, only BS EN 61008-1 and BS EN 61009-1 were still listed (Regulation 411.4.9 refers). However, this does not preclude the use of RCDs to BS 4293, BS 7288 and BS 7071, where appropriate, for fault protection and/or additional protection, provided they meet the relevant operating time requirements.


    Andy B.
Reply
  • The NICEIC, ECA and ELECSA disagree.


    When the 17th Edition (BS 7671: 2008) was published, only BS EN 61008-1 and BS EN 61009-1 were still listed (Regulation 411.4.9 refers). However, this does not preclude the use of RCDs to BS 4293, BS 7288 and BS 7071, where appropriate, for fault protection and/or additional protection, provided they meet the relevant operating time requirements.


    Andy B.
Children
No Data