IET announces new amendment to BS 7671 (IET Wiring Regulations)

Hi all


Just read about this in the latest edition of Wiring Matters Magazine and thought it may be of interest!
Parents
  • SRCDS and SRCDs are intended for additional protection in case of direct contact, therefore they not intended for use when the Zs is to high to blow a fuse in the plug or connection unit, at the point they are connected into the main installation, for example in a TT installation.


    A TT installation has to have an upfront RCD, so you cannot install a SRCD in a TT installation where the circuit it is connected to lacks RCD protection, but there could be a 100 mA RCD upfront of the 30 mA RCD.


    Andy Betteridge
Reply
  • SRCDS and SRCDs are intended for additional protection in case of direct contact, therefore they not intended for use when the Zs is to high to blow a fuse in the plug or connection unit, at the point they are connected into the main installation, for example in a TT installation.


    A TT installation has to have an upfront RCD, so you cannot install a SRCD in a TT installation where the circuit it is connected to lacks RCD protection, but there could be a 100 mA RCD upfront of the 30 mA RCD.


    Andy Betteridge