You can see this plug (with plastic earth pin) on the Diamond stone cutter in Aldi store.
I don't see how it can protect against spikes
A double insulated appliance that desn't have a c.p.c. can't 'see' the voltage difference between line conductors and earth(*) - so a single SPD connected between L and N would provide all the protection it needs.
(* OK it might be able to see the voltage difference between live conductors and true earth if it was left outside on the lawn or somesuch, but then I would expect the substantial plastic case to provide adequate separation)
RCDs are specifically for occasions when a person, or animal, is the earth path.
Just to be absolutely clear in case someone else reads this - RCDs can be used in at least two different ways (sometimes simultaneously) - firstly to provide ADS (usually where the earth loop impedance is too high for overcurrent protective devices to do the job) - in these cases the earth path is intended to be a c.p.c. (not the victim) and potentially allows disconnection to occur before any person or animal risks a shock; and secondly for additional protection where RCDs rated 30mA or below (but never higher rated ones) where the earth path may only be via the victim. UK wiring regs specifically prohibit relying on additional protection alone - it may only be used in addition to ADS (thus requiring a c.p.c. to be present) or some other equally effective measure (such as double/reinforced insulation) - and I would expect appliance standards to follow similar principles.
- Andy.
You can see this plug (with plastic earth pin) on the Diamond stone cutter in Aldi store.
I don't see how it can protect against spikes
A double insulated appliance that desn't have a c.p.c. can't 'see' the voltage difference between line conductors and earth(*) - so a single SPD connected between L and N would provide all the protection it needs.
(* OK it might be able to see the voltage difference between live conductors and true earth if it was left outside on the lawn or somesuch, but then I would expect the substantial plastic case to provide adequate separation)
RCDs are specifically for occasions when a person, or animal, is the earth path.
Just to be absolutely clear in case someone else reads this - RCDs can be used in at least two different ways (sometimes simultaneously) - firstly to provide ADS (usually where the earth loop impedance is too high for overcurrent protective devices to do the job) - in these cases the earth path is intended to be a c.p.c. (not the victim) and potentially allows disconnection to occur before any person or animal risks a shock; and secondly for additional protection where RCDs rated 30mA or below (but never higher rated ones) where the earth path may only be via the victim. UK wiring regs specifically prohibit relying on additional protection alone - it may only be used in addition to ADS (thus requiring a c.p.c. to be present) or some other equally effective measure (such as double/reinforced insulation) - and I would expect appliance standards to follow similar principles.
- Andy.