AJJewsbury:
This cable is BS 7870, split concentric, a distribution (DNO) cable. This is used in a "wiring regulations" environment, if it is not recognised in the regs it must be detailed as a "deviation."
I'd suggest that BS 7671 doesn't have a list of acceptable cable types - although it does (perhaps just for the convenience of the reader) list and provide data for some common types. I think all the cables listed in BS 7671 are for LV use - yet BS 7671 has a much wider scope these days - from SELV door bells to 12V electrics in caravans - yet bell wire isn't listed nor are automotive cables (usually to ISO 6722).
The fundamental requirement is for all items to comply with an appropriate BS or HD, or in the absence of such a standard to an international standard or appropriate standard of another country. If a cable meets any of those, there's no deviation.
Of course a cable needs to be suitable for its intended purpose - and just complying with some random BS is no guarantee of that.
- Andy.
No. Appendix 1 includes only those standards which are included in BS 7671 and Appendix 4 is informative not normative.
Split concentric cable in the LV range complying with either one of two British Standards - BS 4553 and BS 7870 - may be selected, if appropriate to the intended use, without infringing the requirements of BS 7671.
Split concentric thermoplastic insulated and sheathed cable is listed in Table F4 of IET Guidance Note 1, Selection and Erection as one of the types of cable that can be used for fixed wiring.
Split concentric cables can be used in consumers' premises, provided they comply with the relevant cable standard and are installed in accordance with the requirements of BS 7671. Some types of terminal and clamping unit are unsuitable for the multiple neutral conductors of split concentric cable. Consequently, installers must take account of instructions for terminations provided by the manufacturer of the distribution board / consumer unit.
Regulation number(s):
- 133.1.1
- 510.3
- 511.1
"split concentric cables can be used on consumers premises"
"but a building network, by definition, isn't a consumers installation"
"it doesn't (to me) seem to fit the definition of "consumer" More likely its just a type of "distributor"