Ring Main Joint Box

A kitchen worktop twin S,O, is to be relocated horizontally by about 60cm. 

The ring final cct (RFC) is cabled in buried T&E and the galv' steel back-box is flushed into the plaster/brick wall.

The RFC T&E extension cabling will be buried under plaster, covered in plastic capping along the horizontal  prescribed zone. Visually, it would be reasonable for an electrician to be aware that the route may contain cable(s).

The circuit is RCD protected.

The intent is touse insulated crimp and double insulating tape the jointed cables within the existing box to achieve a maintenance free connection, A 2mm thick (fabricated) plate was to be used to cover the back box and provide additional mechanical protection. The box would then be plastered over.


The questions are:-

1. How many would consider the steel plate back box cover a desirable feature or would a simple plastic cover suffice?

2. Should the original back box be left  unearthed?


Thanks in advance.
Parents

  • PG:




    Typiod:

    if you are moving the socket horizontally from its original position what is there to signify the original drop to the original socket?




    You are correct, all the existing sockets are actually dropping from the ceiling (all concealed by plaster). The circuit extension under discussion would be horizontal - but still within the prescribed zones depicted in the OSG. My point was that it shouldn't be a surprise for someone who was aware of prescribed zones.


     




     

    There will not be any indication where the existing drop to the box that is going to be concealed is.


    Andy Betteridge
Reply

  • PG:




    Typiod:

    if you are moving the socket horizontally from its original position what is there to signify the original drop to the original socket?




    You are correct, all the existing sockets are actually dropping from the ceiling (all concealed by plaster). The circuit extension under discussion would be horizontal - but still within the prescribed zones depicted in the OSG. My point was that it shouldn't be a surprise for someone who was aware of prescribed zones.


     




     

    There will not be any indication where the existing drop to the box that is going to be concealed is.