PME earthing to a group of static caravans TT earth required?

Can anyone give me there valuable opinions on earthing to a static-mobile home please. As per BS7671, PME earthing is not allowed to (mobile) caravans. However, does a static caravan (plumbed in and permanent with a SWA cable supplying it and no plug/socket arrangement) count as a caravan. The Static caravan is metal framed, and placed some distance from the PME source 40m or so, and the cable size is 16mm CSA 3 core, so PME (100A single phase) could be exported on the cable as its greater than 10mm CSA,

The static caravan is permanent and not quite the same as a transportable caravan, so does a TT earth need to be installed?
Parents
  • Immediate kneejerk response is ... definitely needs an earth rod per caravan (metal frame WILL be introducing true earth)... and the requirements for TT seem less onerous in this example?
Reply
  • Immediate kneejerk response is ... definitely needs an earth rod per caravan (metal frame WILL be introducing true earth)... and the requirements for TT seem less onerous in this example?