conflicting information on bathroom fan in zone 1.

Have been on an eicr today and noted a 230v IP44 mainrose intervent BVT  100wall fan about 150mm horizontal from a movable shower head

in zone 1.According to the BBB ,IPx4 fans are ok in this zone.However,when I check online,Mainrose state "the fan should not be

accessable to a person using the shower and be over 1800mm high"So I suppose manufactures instructions hold sway.In the

past I,ve always fitted elv fans in this situation.Wondered what others think.

                                                                                                                     Regards,Hz
Parents
  • this from the manrose site http://www.manrose.com/fan_select.htm# under "siting the fan"

    Alternatively, the new Manrose range of 12 volt S.E.L.V. (Safety Extra Low Voltage) fans are specifically designed for the safe ventilation of toilets, bathrooms and shower rooms and can be fitted within the splash area with absolutely no risk of
    electric shock.



     most of the other fans state the same as you mentioned.
Reply
  • this from the manrose site http://www.manrose.com/fan_select.htm# under "siting the fan"

    Alternatively, the new Manrose range of 12 volt S.E.L.V. (Safety Extra Low Voltage) fans are specifically designed for the safe ventilation of toilets, bathrooms and shower rooms and can be fitted within the splash area with absolutely no risk of
    electric shock.



     most of the other fans state the same as you mentioned.