conflicting information on bathroom fan in zone 1.

Have been on an eicr today and noted a 230v IP44 mainrose intervent BVT  100wall fan about 150mm horizontal from a movable shower head

in zone 1.According to the BBB ,IPx4 fans are ok in this zone.However,when I check online,Mainrose state "the fan should not be

accessable to a person using the shower and be over 1800mm high"So I suppose manufactures instructions hold sway.In the

past I,ve always fitted elv fans in this situation.Wondered what others think.

                                                                                                                     Regards,Hz
Parents
  • 701.55 applies. In zone 1, only the following fixed and permanently connected current using equipment shall be installed, PROVIDED IT IS SUITABLE FOR INSTALLATION IN ZONE 1 ACCORDING TO THE MANUFACTURER's INSTRUCTIONS.