Just wondered  why these are not classed as "similar switchgear" to consumer units etc which are supposed to be in

non flammable enclosures in domestics.

                                          Regards,Hz
Parents
  • When the DNO installs the isolator, they don't have to comply with BS 7671.


    When it becomes the consumers afterwards, and is inspected against BS 7671, the game changes ...